If you turn on “Connect adjacent rooms” under “Advanced settings” you will get thermal conduction between the zones. The distance between the zones does not have to be exactly the same as the wall thickness for the zones to be thermally connected through their common wall. Largest allowed distance is 0.5 m horizontally and 0.8 m vertically. Larger distance will give separate adiabatic walls.
If you don’t turn on “Connect adjacent rooms” (default) the inner walls will be adiabatic, but you will still have thermal interaction (storage) with half of the wall. In both cases you should model the inner walls with their full thickness.