1 | initial version |
ESBO Light does not support a "pure" overheating calculation in the sense of automatically finding the highest room temperature for a case with ventilation but without any central or local mechanical cooling. Using default (ASHRAE) climate data, it will always find the month that requires the highest amount of room cooling, whether it is mechanical or not. At Level 2, you can remove room as well as central cooling (delete the chiller object) and for this input, the presented monthly design day will be the one where the (uncooled) ventilation air cools the room the most (not necessarily the one with the highest room temperature).
In order to bypass the algorithm that automatically finds the month with the highest room cooling, you can open the Location object, and press User defined design days. Accept the default temperatures (the warmest of the ASHRAE summer days is default), press Save as and give the new Location object a new name. The cooling design calculation will now only compute this single hot day.
As another alternative, you can select a fixed supply air temperature and a small supply air flow, the air handling unit mechanical cooling will now be very small (have negligible effect on room temperature) and you will find the month with the highest indoor temperature.
Sorry for the long answer, but this is a bit complicated.