Ask Your Question
0

I don't get enough heat out of the radiator

asked 2016-03-01 14:57:24 +0000

anonymous user

Anonymous

In my case, the needed power to heat the room is 1400 W and I have selected a radiator to deliver this. However, in the Heating design simulation with this radiator, the actual radiator power is only 900 W and this is not enough to heat the room.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2016-03-01 15:04:40 +0000

Per Sahlin gravatar image

updated 2018-02-14 08:53:02 +0000

The size of the radiator is given with respect to some (editable) rated temperature conditions (see image below) and it will deliver the needed heat only if the actual supply water temperature is high enough. First, check the supply temperature curve to the radiator. This is given under Heat on the Building tab. If the supply temperature setpoint is high enough, make sure that your Topup heating unit is able to deliver sufficient power.

image description

edit flag offensive delete link more
Login/Signup to Answer

Question Tools

1 follower

Stats

Asked: 2016-03-01 14:57:24 +0000

Seen: 3,080 times

Last updated: Feb 14 '18